Quote:
Originally Posted by RonL View Post
I believe that I saw somewhere that if you tighten down the side screws on back stabbed outlets it tightens against the back stabbed wire. I have a circuit that I just pulled out that that was working intermittently that I need to shut the breaker and see if this is true.
I dont know if it is true either but I have heard the same thing bout the back stabbed outlets. But, I always use the screws and screw the wires down since I dont trust the wire stab portion.
__________________
I love the smell of napalm in the morning. It smells like, victory!
Rommel, you magnificent bastard, I read your book!
Still got the shovel!

Victor Torch Set With Meco Regs
Lincoln Weld Pak 100
Giant Tech Arc 200
Miller Roughneck2E
Reply With Quote
  #12  
Old 07-16-2022, 08:43 PM
Norcal Norcal is offline
Elite Member
 
Join Date: Jul 2009
Location: California
Posts: 1,815
Default

Quote:
Originally Posted by astronut View Post
I dont know if it is true either but I have heard the same thing bout the back stabbed outlets. But, I always use the screws and screw the wires down since I dont trust the wire stab portion.
While I am not a fan of backstabbed/push and pray connections, have taken out large numbers of 50 year old Eagle Electric backstab only receptacles that were in good condition other then being worn out, (poor plug retention) but the brass tabs were wider then current production.
Reply With Quote
  #13  
Old 07-16-2022, 10:17 PM
Shade Tree Welder's Avatar
Shade Tree Welder Shade Tree Welder is offline
Grumpy Bastard
 
Join Date: Jun 2004
Location: Kankakee County, IL
Posts: 22,245
Default

Quote:
Originally Posted by RonL View Post
I believe that I saw somewhere that if you tighten down the side screws on back stabbed outlets it tightens against the back stabbed wire. I have a circuit that I just pulled out that that was working intermittently that I need to shut the breaker and see if this is true.
Quote:
Originally Posted by astronut View Post
I dont know if it is true either but I have heard the same thing bout the back stabbed outlets. But, I always use the screws and screw the wires down since I dont trust the wire stab portion.
Your talking about 2 different outlet types.

True back stabs are just that for solid wire where the only thing holding the
wire is spring tension inside the recpt.

The ones where you can tighten the screw are a pressure plate design and
are not back stab. Even is it kinda looks the same they are very different.
The pressure plate design is a very good design.
__________________
Shade

"Prepare to defend yourselves."
-- Sergeant Major Basil L. Plumley, Ia Drang Valley
Reply With Quote
  #14  
Old 07-17-2022, 08:42 AM
Norcal Norcal is offline
Elite Member
 
Join Date: Jul 2009
Location: California
Posts: 1,815
Default

There are 4 ways of connecting receptacles.

1) Screws, wire is wrapped around a screw, used on the budget devices. CO/ALR devices are also this way CO/ALR, is the designation for 15/20A devices rated for copper or aluminum conductors, AL/CU is the marking for 30A & above devices rated for copper or aluminum conductors.

2) Backwire, "push and pray" used with #1 as current UL standard require that 14 AWG is the maximum wire gauge used with backwire, in the past there were backwire only that would accept 12 AWG, & some would accept 10 AWG.

3) Pressure plate, wire stripped to the proscribed length is inserted into the back of the device and a plate attached to a captive screw is tightened to secure the conductor.

4) Pigtail, a length of wire is factory installed on a device, early GFCI receptacles were equipped that way, some higher end devices are available that way, but quite rare.


Push and pray is for solid copper conductors only, pressure plate terminals can be used with solid or stranded copper conductors.

Last edited by Norcal; 07-17-2022 at 08:49 AM.
Reply With Quote
  #15  
Old 07-17-2022, 09:21 AM
Shade Tree Welder's Avatar
Shade Tree Welder Shade Tree Welder is offline
Grumpy Bastard
 
Join Date: Jun 2004
Location: Kankakee County, IL
Posts: 22,245
Default

Nocal, thanks for saying it better.
__________________
Shade

"Prepare to defend yourselves."
-- Sergeant Major Basil L. Plumley, Ia Drang Valley
Reply With Quote
  #16  
Old 09-13-2022, 10:38 PM
Don_S Don_S is offline
Senior Member
 
Join Date: Mar 2005
Location: Tenville, IA
Posts: 561
Default

I will say that the PSL decorator 15 A outlets that come in the contractor packs at the big box stores are junk. The face plates fall off. I replaced with commercial grade outlets at the places that get any traffic. The jury is still out on those.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Web Search:

All times are GMT -5. The time now is 10:05 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2022, vBulletin Solutions Inc.