Default Todays Worthless Time Consuming Job - Yet Another VFD Failure

We sell a brand of boilers (that shall remain nameless, to protect the guilty), that lately have had their share of service/parts problems. I was called out to a jr-high school, with a boiler in alarm, from the fault codes and the smell, it became apparent it was another motor/VFD failure. This make about at least 2 dozen of these failures, over the last 6-8 months, in our service area The VFD manufacturer also manufactures the motor, this is an inverter VFD, single phase 230 vac single phase in and 220 vac 3 phase out, the truly bad part is there doesn't seem to be any early warning of disaster, they just go bang. The manufacturer is one of the worlds largest electrical concerns and had been making VFDs for over 40 years, in many forms, and they are completely baffled. This particular VFD is factory programed, and the basic program is locked, with only about 10 variables that are field changeable ( we don't change them, they are left at factory defaults). They are sending a new motor and VFD, its about a 3 hour change out and at this point I can't guaranty it will last until I get to the end of the drive way.

I install VFDs all of the time and failures are not uncommon, usually because of wrongful applications, wrong types of motors or operational issues, but this boiler package was designed from the beginning as a package and to this point nothing concrete has shown up as the cause of the failures. There is nothing harder in the world to tell a customer it has failed, they sending new parts and you hope it cures the problem.
__________________
jack
Reply With Quote
  #2  
Old 12-04-2009, 08:13 PM
Charlie C's Avatar
Charlie C Charlie C is offline
More STEAM!!
 
Join Date: Dec 2006
Location: Southern Oregon
Posts: 6,036
Default

I feel for you Jack, having to tell the customer that there is a failure and it is your equipment. That is a bummer for sure.
Reply With Quote
  #3  
Old 12-04-2009, 08:39 PM
Scotts's Avatar
Scotts Scotts is offline
Stuff, Just stuff
 
Join Date: Dec 2004
Location: Wichita Kansas
Posts: 5,283
Default

Jack is it a powerflex drive?

I won't name the mfg either. You will know or you won't know.

Scott
Reply With Quote
  #4  
Old 12-04-2009, 08:40 PM
GWIZ's Avatar
GWIZ GWIZ is offline
SFT Historian
 
Join Date: Feb 2006
Location: USA
Posts: 7,095
Default

What size motor ?
__________________
*
*
The factory of the future will have only two employees, a man and a dog. The man will be there to feed the dog. The dog will be there to keep the man from touching the equipment. ~Warren G. Bennis
Reply With Quote
  #5  
Old 12-04-2009, 08:53 PM
platypus20's Avatar
platypus20 platypus20 is offline
Boiler God
 
Join Date: Aug 2007
Location: camillus, ny (syracuse)
Posts: 9,838
Default

Quote:
Originally Posted by Scotts View Post
Jack is it a powerflex drive?

I won't name the mfg either. You will know or you won't know.


Scott
No, not a powerflex, its a European unit

Quote:
Originally Posted by GWIZ View Post
What size motor ?
The sizes of the motors have varied, the one today was 1.25 hp


jack
__________________
jack
Reply With Quote
  #6  
Old 12-04-2009, 09:23 PM
cutter's Avatar
cutter cutter is offline

12-29-1943 to 1-17-2020
Curmudgeon emeritus
 
Join Date: Jun 2004
Location: Lubbock,Texas
Posts: 33,114
Default

I suppose there are several of these units of different hp & configuration in each boiler installation so it'd be impractical for the customer to keep a backup on hand?
__________________
cutter
Housekeeping Staff: the Gatekeeper
Director of Policy, Syntax and Grammar (by appointment)

"Dr. Chandran, will I dream?"

Just Keep Walking

"I am not a body, I am free.
For I am still as God created me."
Reply With Quote
  #7  
Old 12-04-2009, 09:37 PM
Scotts's Avatar
Scotts Scotts is offline
Stuff, Just stuff
 
Join Date: Dec 2004
Location: Wichita Kansas
Posts: 5,283
Default

Quote:
Originally Posted by platypus20 View Post
No, not a powerflex, its a European unit



The sizes of the motors have varied, the one today was 1.25 hp


jack
close enough. Are these units equipped with a cooling fan on the drive? If they are they may have their very own drive to regulate the speed of the cooling fan. A drive within a drive so to speak. The drive is sized very close to size of the application. Actually the drive depends on the cooling fan to cheat a little on the size and cost. Several of these at our home office have melted down due to the drive for the cooling fan going out and thus toasting the drive in quite the short order.

The OEM out there just gave up and supplied a drive from a different manufacturer. Issue resolved.

Scott
Reply With Quote
  #8  
Old 12-04-2009, 10:10 PM
Ironman's Avatar
Ironman Ironman is offline
Iron Modification Investigator
 
Join Date: Feb 2008
Location: Warburg, Alberta, Canada
Posts: 14,924
Default

There may be a way to find out the problem. There is a type of breaker made for 3 phase, we used them on Flygt pumps alot...that trips out on any phase imbalance. (prevents 2 phasing, the death blow to motors.
If this was installed between the VFD and the motor, you could find out fast if the motor was failing and destroying the VFD, or the VFD failed and the motor was okay.
They always tell you to switch the VFD only, but this would only activate on failure of one or the other component.
__________________
Gerry
You got freedom of speech, if you don't say too much.
Aaron Neville.

The virtue is always a cover for the sin. That's the key to understanding the modern left. Whatever they're accusing you of doing, they are doing themselves but more enthusiastically. And that's definitely the story of Justin Trudeau. Tucker Carlson
Reply With Quote
  #9  
Old 12-05-2009, 09:43 AM
rmack898's Avatar
rmack898 rmack898 is offline
That HURT!
 
Join Date: Feb 2006
Location: Honu Grove (NE Florida)
Posts: 4,035
Default

Quote:
Originally Posted by Ironman View Post
If this was installed between the VFD and the motor
Gerry, someone correct me if I'm wrong but I was always under the impression that any switching device between the VFD and the motor would kill the VFD in short order.
__________________
Mac
___________________________________________
One extremely happy former convict of the penal colony that lies between NY, PA, and DE. Now living the good life much further south. where they don't know what fucking Carhartts are.
Reply With Quote
  #10  
Old 12-05-2009, 12:53 PM
Ironman's Avatar
Ironman Ironman is offline
Iron Modification Investigator
 
Join Date: Feb 2008
Location: Warburg, Alberta, Canada
Posts: 14,924
Default

Quote:
Originally Posted by rmack898 View Post
Gerry, someone correct me if I'm wrong but I was always under the impression that any switching device between the VFD and the motor would kill the VFD in short order.
Yes, you are right.
I'm not saying use the switch as a shut off device. I'm saying use it's phase loss protection system. If this thing trips, you are already in trouble. You have lost a motor or a phase from the VFD.
So it's tripped ....measure voltage on the VFD...is it toast? If not....measure the motor windings....is it toast?
At this point you can determin if the motor is failing every time ...or the VFD

Some motors are not rated for VFD service...and this may be killing the motor and the VFD.
__________________
Gerry
You got freedom of speech, if you don't say too much.
Aaron Neville.

The virtue is always a cover for the sin. That's the key to understanding the modern left. Whatever they're accusing you of doing, they are doing themselves but more enthusiastically. And that's definitely the story of Justin Trudeau. Tucker Carlson
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Web Search:

All times are GMT -5. The time now is 03:09 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2020, vBulletin Solutions Inc.