Default running your own gas pipe...

Anyone here done gas plumbing? Is it something that is safe to DIY?

I am looking to pipe in an LP range for a buddy, and from what I can tell, it looks pretty simple.

Pipe dope, instead of teflon tape. Pipe straps every 8' (for 3/4" pipe) Outside termination can't be any closer than 6" from the ground. To thread, I read somewhere you go as tight as you can by hand, then wrench it 1 full turn, much tighter can distort the pipe, since they are tapered threads.

spray the joints with soapy water after charging the line with 15psi of air and check for bubbles..., and a WOG rated valve(means water oil and gas?)

It looks pretty simple, but I don;t want to blow myself up either. I can't justifying paying some guy $100 an hour to do something that has 3 elbows.


Am I nuts? (for thinking about doign it myself, not for all the other reasons that are obvious in my character.) Am I missing anything important?
__________________
Director of Redundancy Director (self appointed)
Reply With Quote
  #2  
Old 07-09-2006, 09:18 PM
boilerman's Avatar
boilerman boilerman is offline
SFT Brewmaster
 
Join Date: Jun 2004
Location: Marshallville,Ohio
Posts: 3,360
Default

Quote:
Originally Posted by Jake
Anyone here done gas plumbing? Is it something that is safe to DIY?

I am looking to pipe in an LP range for a buddy, and from what I can tell, it looks pretty simple.

Pipe dope, instead of teflon tape. Pipe straps every 8' (for 3/4" pipe) Outside termination can't be any closer than 6" from the ground. To thread, I read somewhere you go as tight as you can by hand, then wrench it 1 full turn, much tighter can distort the pipe, since they are tapered threads.

spray the joints with soapy water after charging the line with 15psi of air and check for bubbles..., and a WOG rated valve(means water oil and gas?)

It looks pretty simple, but I don;t want to blow myself up either. I can't justifying paying some guy $100 an hour to do something that has 3 elbows.


Am I nuts? (for thinking about doign it myself, not for all the other reasons that are obvious in my character.) Am I missing anything important?
unless your a moron i think you'll be ok...don't forget your dirt legs
__________________
Director of Recruitment, Overseas (by appointment)

I don't suffer from insanity...I enjoy every minute of it
---------------------------------------------------
Reply With Quote
  #3  
Old 07-09-2006, 10:12 PM
sbi1's Avatar
sbi1 sbi1 is offline
Senior Member
 
Join Date: Dec 2005
Location: Middlesex, NC
Posts: 279
Default

Are you plumbing it into an existing gas system, or a small tank just for the range? It sounds like you've got the piping pretty well figured out, the only thing that I would do different is that when you pressurize the line, leave a pressure guage on it. Let it sit for 15 min., if there is no drop in pressure, no leaks. One caution on pressure testing-leave the cutoff at the range closed. Most appliances are not rated for more than 2 psi, so a 15 psi pressure test can damage them. I don't know what the permit or inspection requirements are in your part of the country, so you may want to check on that locally. Around here, a lot of gas piping is done without permits even when they are required.
__________________
sbi1
Good judgement comes from experience.
Experience comes from bad judgement.
Reply With Quote
  #4  
Old 07-09-2006, 11:16 PM
bgott bgott is offline
Trailers for sale or rent
 
Join Date: Mar 2005
Location: Houston, TX.
Posts: 1,574
Default

There is a gas rated teflon tape available, it's the yellow stuff. Don't use galvanized, use black iron pipe. I run a pipe support every 4', I believe I read in my plumbing book ( out on loan, so I can't verify) that 4' is code in a lot of places.
Reply With Quote
  #5  
Old 07-10-2006, 09:59 AM
standles standles is offline
Member
 
Join Date: Mar 2006
Location: Florida
Posts: 112
Default

At least in my neck of the woods...

You can do it yourself as it is no big deal as long as you PSI check with compressed air.

HOWEVER....

The local NG gas company will not hook up service (and it is a fineable offense if you hook it up yourself) unless a certified plumber did the work or you have one sign off on it. The signing off on I tried but most would not as it transfers liability to them if they certify it and it turns up bad.



You mileage may vary of course.



Now if it is propane then you probably could since the NG company is not involved.


Steven
__________________
Inspiring Thought for the Day:

Some people are like slinkies ... Not really good for anything....but they still bring a smile to your face when you push them down a flight of stairs.
Reply With Quote
  #6  
Old 07-10-2006, 12:01 PM
Jake's Avatar
Jake Jake is offline
Holder of only Official Titles
 
Join Date: Jun 2004
Location: North of Pile Buck
Posts: 1,256
Default

Thanks, I feel better about attemptins this, and since I am only mildly retarded... I suspect it will go well. It is propane, so I am the only one who's inspection it has to pass.
__________________
Director of Redundancy Director (self appointed)
Reply With Quote
  #7  
Old 08-01-2006, 01:28 AM
Jake's Avatar
Jake Jake is offline
Holder of only Official Titles
 
Join Date: Jun 2004
Location: North of Pile Buck
Posts: 1,256
Default

ok...So I ran the pipe... pressure tested it 15 lbs for 1/2 hour... did fine. left the air in and came back today, guage at 12... is that bad?

Not only that, but I spent all day farting around with nipples and 90's to make it go around a corner and off a deck, and the guy says,"can you just drill a hole in the deck and go straight down? It's only money man... it's only money. So I will have to redo part... Still though, what about losing 3 lbs over the weekend.. is that something to worry about? I think the actual pressure is .5 lbs or something like that.... could I have lost that through the ball valve in the kitchen?

I did build a tricky deal though... I took a piece of 3/4 black pipe and welded a washer to the end. Ran a piece of roundstock though that and welded the roundstock to an old forsner bit (1 1/4") and used the pipe to center and push the drill bit the length of the wall I was drilling... the result was a nice straight line of holes through the wall and no fighting black pipe to get it through the wall...

I think when I am done, I will use it to harpoon a whale... I kinda looks like one....
__________________
Director of Redundancy Director (self appointed)
Reply With Quote
  #8  
Old 08-01-2006, 07:14 AM
b-footn's Avatar
b-footn b-footn is offline
Yes girls, he's single!
 
Join Date: Feb 2005
Location: Nashville, TN
Posts: 1,163
Default

Losing pressure is bad, but a lot of things can affect it. Temperature differences between night and day will bring the gauge down, but it will come back up as the temperature rises. I have seen some new gauges that will have a slow leak inside the gauge.
__________________
Life is not a journey to the grave, with the intention of arriving safely, in one pretty and well-preserved piece, but to skid in broadside, thoroughly used up, worn out and shouting WOW...what a ride
Reply With Quote
  #9  
Old 08-01-2006, 07:35 AM
moe1942's Avatar
moe1942 moe1942 is offline
Voice of Experience
 
Join Date: Jun 2004
Location: Alexandria, Louisiana
Posts: 11,236
Default

If it holds pressure for 15 minutes consider it a done deal. Foot cited a few things that would affect pressure over that length of time. Also, if you still are worried do a soap test at all joints. But that is why they put mercapton? in NG.

If all else fails your nose will alert you..

Most areas of the country don't run more than 1/4 PSI. You could hand tighten the joints using rector seal and not get a leak...
__________________
Don't pick a fight with an old man. If he is too old to fight, he'll just kill you... John Steinbeck

"If we ever forget that we're one nation under God, then we will
be a nation gone under". ~Ronald Reagan

We should have picked our own cotton...

I love my women hot and my beer ice cold..
Reply With Quote
  #10  
Old 08-01-2006, 12:44 PM
Jake's Avatar
Jake Jake is offline
Holder of only Official Titles
 
Join Date: Jun 2004
Location: North of Pile Buck
Posts: 1,256
Default

Well, I will re-run the pipe down through the deck and re-test it, then we will see how it works...

THanks for the advice guys... this is easier than I thought it would be. You think gas, and you can get freaked out, but it was't that tough.
__________________
Director of Redundancy Director (self appointed)
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Web Search:

All times are GMT -5. The time now is 08:49 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2023, vBulletin Solutions Inc.