Originally Posted by Norcal View Post
Attachment 159054

That label is not a "scam" the manufacturer has calculated the load of the equipment plus added the required 125% so the electrician sizes the conductors based on 22A,
Not being specific to TRANE

there was two labels. I'm talking about a label that the "Manufacturer" states what wire size to use. I don't see a wire size listed in the label you posted.